Hi, is there any option to set offset for this tweak option? I would like to set target temp =20.5 and expect from TRVs turn off when temp=21 and turn on when temp=20. My main problem is working of my new Moes BRT-100 TRVs which start heating when temp is 0.5 below target but close valves when temp is 2° above target which is unacceptable due to heating costs. When I use this integration in 'normal' way valves are still open even the temp on thermometer is much higher than target. |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments
-
|
Hey, that's why aggressive mode exists. You can define a range around your target temperature let's say 0.2°C and an offset e.g. 2°C. If your target temperature is 20°C there is a range from 19.8 - 20.2°C. This is exactly designed for that use case and you can disable Off If Above/Below Room Temperature. |
Beta Was this translation helpful? Give feedback.
-
|
Ah, that's how it works.. Perfect, now it works great. Thank you :) |
Beta Was this translation helpful? Give feedback.
Hey, that's why aggressive mode exists. You can define a range around your target temperature let's say 0.2°C and an offset e.g. 2°C.
If your target temperature is 20°C there is a range from 19.8 - 20.2°C.
If your local temperature is below this range the offset is added to the target temperature -> 22°C
If the local temperature hits the range the target temperature is set without the offset -> 20°C
If the local temperature is above that range, e.g. 20.3°C the offset is subtracted from the target temperature -> 18°C
This is exactly designed for that use case and you can disable Off If Above/Below Room Temperature.